In message <57441ACA.8070609 at arcor.de>, Gerhard Hoffmann writes:
>Am 23.05.2016 um 05:15 schrieb Jim Palfreyman:
>> As far as a remedy goes we are going to try a solid state relay that only
>> switches on at 0V in the AC waveform. This should slow the inrush current,
>> and hopefully the magnetic impulse.
>>
>>
>In the context of transformers and motors, switching on at 0V is
>actually the worst point in time.
Well...
The motor is almost certainly an "Squirrel-cage" induction motor and
that means it is three phase, although one of the phases is probably
created with a "starting capacitor".
So which of the three phases is going to be the lucky one that
switches at maximum voltage, or are you going to switch the phases
on sequentially ?
A 4kW Variable Frequency Drive costs less than $1k and allows you
to control *both* the voltage/time and the frequency/time *both*
during startup and during rundown.
I wouldn't bother fuzzing around with hacks - I'd just go for the
known-to-work solution.
--