[volt-nuts] Curious overvoltage event

Chuck Harris cfharris at erols.com
Mon Aug 10 10:22:47 EDT 2015


It is a common failure in many switching power supplies to expect that
the power line voltage will snap on quickly, and snap off quickly when
the supply is activated, or deactivated.

If the mains supply hangs around in certain brown out voltage ranges, it
can fool the start up control circuitry into exceeding the ratings on
the bootstrap circuitry, or the inrush limiting circuitry, and toast parts.

Better supplies have timers that make sure that the inrush protection,
or boot strap power only last for the amount of time expected, and
shut down if those values are exceeded.

The usual UPS can be complicit in these failures because they just pass
the mains power through to the load, and don't switch over to inverter power
until a programmed amount of brown out has occurred... if at all.

Basically they pass the crappy brown out power on to the load.

-Chuck Harris


Andrea Baldoni wrote:
> Dear fellow experimenters, hello.
>
> Yesterday, in the zone near my lab, the weather forecast was of a big storm.
> I was here doing some work when the sun got covered by clouds and started
> a strong wind. The neon lights went away for a fraction of a second, not
> enough for the PC to reset, then, something like ten seconds later, the lights
> went out, I heared a multiple clicking sound from the electric switch box, then
> the UPS alarm.
> I thought it was a blackout, but no, the UPS was in "overload alarm", there
> was smell of something burned and all chain of three automatic switches
> powering it tripped.
>
> It turned out that the power supply of my server, protected by the "line
> interactive" UPS burned out. I opened it, and the chain of resistors and
> diodes giving the startup power to the control IC UC3843 arched and the IC
> itself exploded (more details on the circuit later on request, I still didn't
> reverse engineer it).
> To this point, nothing exceptional: an overvoltage came from the line and,
> even if nothing else of the many devices in the lab (fortunately) had been
> affected, this power supply died. I didn't saw any lightning however and no
> thunder.
>
> The strange thing came this morning, when a customer, having the office
> 19Km far from my lab in a zone populated enough to have between us some small
> towns and industrial areas, called because his server was off. Guess? Exactly
> the same power supply, exactly the same components arched, and the control IC
> exploded in the same way. Also in their office, no other equipment was
> affected, everything was running and the UPS didn't went into overload alarm
> (or maybe it did and recovered by itself, I don't know in effect).
>
> Surely we are on the same grid, even if the transformers are obviously
> different, but despite I have other customers in the zone (none with the same
> power supply model), I didn't get any other call (while usually I do, when a
> lightning strike), and, no one reported to me to have had problems with other
> equipment.
>
> Now I just had the idea to check the logs of the servers to see if they powered
> off at the same time. They did not, the one of my customer powered off
> 17 hours earlier, when the storm was still far away (it's unlikely the sudden
> power off erased 17 hours of logs).
>
> Could be just a coincidence?
>
> Best regards,
> Andrea Baldoni