[time-nuts] Lady Heather
ws at Yahoo
warrensjmail-one at yahoo.com
Fri Jul 13 22:52:01 UTC 2012
Don
No, it is not bang-bang. Look at the plot results.
You don't get .001 deg type resolution and control with a bang-bang controller.
It is a full Linear, universal, PID + with self tuning capability.
The output is a high resolution Linear PWM driving one of the RS232 pins and a polarity/enable
output on one of the other pins which can be used for heating / cooling / enable / fail_ save, etc.
( I don't use the second output with the KISS simple fan driver, because that hardware is already fail-safe).
The PID can be manually set for all kinds of things, Including Band-Bang control.
ws
****************
Thanks, Warren, for the refresh. So the L.H. fan control signal is
bang-bang, and not really a PID, as it's on the DTR data line.
Don
ws at Yahoo
> Don
>
> no internal connection needed.
> Lots of ways to do it,
> an isolated optical isolator connect to a couple of pins on the RS232
> connector is one way.
>
> The LH controller can also be used to just Heat for those that don't
> like
> moving parts,
> or dual with heat and cool as well as just drive a fan.
> If ypu want you could go full nuts and connect it up to control the room
> AC/Heater
>
> For the LH driver I use and how I use it see:
> <http://www.febo.com/pipermail/time-nuts/attachments/20110116/76cc81b5/attachment-0001.jpg>
>
> text at:
> <http://www.febo.com/pipermail/time-nuts/2011-January/053648.html>
>
> ws
>
> *******************